DLMS Disconnect Control (Class 70) Remote Cut-off and Reconnection State Machine
-
Engineering Guide: Disconnect Control (Class 70)
Managing internal contactors for demand limiting or prepayment requires strict adherence to the Class 70 state machine defined in IEC 62056-62.
Object Identification
- OBIS Code:
0.0.96.3.10.255(Disconnect Control 1) - Class ID:
70
Control Methods
- Method 1 (
remote_disconnect): Opens the contactor (Disconnects supply). - Method 2 (
remote_reconnect): Closes the contactor or enters 'Ready for Reconnection' state.
Output State Validation (Attribute 2)
Control State Value Meaning Physical Contactor Status 0Disconnected Open (No power) 1Connected Closed (Power active) 2Ready_For_Reconnection Open (Awaiting manual button press on meter) [!IMPORTANT]
Safety regulations in many jurisdictions forbid immediate remote closure if someone is working on site. Settingcontrol_mode = 2transitions the meter to state2, requiring the consumer to press the meter physical push-button to complete the circuit. - OBIS Code:
-
From field experience: Always read Attribute 3 (
control_state) immediately after executingremote_reconnect. If the meter is configured in Safety Mode, the state will read2(Ready_For_Reconnection) rather than1(Connected). The consumer display will show a blinking reconnect icon. -
In the meter firmware, contactor pulse duration is controlled via Attribute 4 (
output_signal). We configure a 200ms pulse for the magnetic latching relay to prevent coil overheating.
Hello! It looks like you're interested in this conversation, but you don't have an account yet.
Getting fed up of having to scroll through the same posts each visit? When you register for an account, you'll always come back to exactly where you were before, and choose to be notified of new replies (either via email, or push notification). You'll also be able to save bookmarks and upvote posts to show your appreciation to other community members.