DLMS Disconnect Control (Class 70) Remote Cut-off and Reconnection State Machine

Scheduled Pinned Locked Moved General Discussion
disconnect-contclass-70relayprepaymentremote-cut
3 Posts 3 Posters 16 Views 1 Watching
  • Oldest to Newest
  • Newest to Oldest
  • Most Votes
Reply
  • Reply as topic
Log in to reply
  • D Offline
    D Offline
    david_miller
    wrote on last edited by
    #1

    Engineering Guide: Disconnect Control (Class 70)

    Managing internal contactors for demand limiting or prepayment requires strict adherence to the Class 70 state machine defined in IEC 62056-62.

    Object Identification

    • OBIS Code: 0.0.96.3.10.255 (Disconnect Control 1)
    • Class ID: 70

    Control Methods

    • Method 1 (remote_disconnect): Opens the contactor (Disconnects supply).
    • Method 2 (remote_reconnect): Closes the contactor or enters 'Ready for Reconnection' state.

    Output State Validation (Attribute 2)

    Control State Value Meaning Physical Contactor Status
    0 Disconnected Open (No power)
    1 Connected Closed (Power active)
    2 Ready_For_Reconnection Open (Awaiting manual button press on meter)

    [!IMPORTANT]
    Safety regulations in many jurisdictions forbid immediate remote closure if someone is working on site. Setting control_mode = 2 transitions the meter to state 2, requiring the consumer to press the meter physical push-button to complete the circuit.

    1 Reply Last reply
    0
    • C Offline
      C Offline
      carlos_mendez
      wrote on last edited by
      #2

      From field experience: Always read Attribute 3 (control_state) immediately after executing remote_reconnect. If the meter is configured in Safety Mode, the state will read 2 (Ready_For_Reconnection) rather than 1 (Connected). The consumer display will show a blinking reconnect icon.

      1 Reply Last reply
      0
      • E Offline
        E Offline
        elena_rostova
        wrote on last edited by
        #3

        In the meter firmware, contactor pulse duration is controlled via Attribute 4 (output_signal). We configure a 200ms pulse for the magnetic latching relay to prevent coil overheating.

        1 Reply Last reply
        0

        Hello! It looks like you're interested in this conversation, but you don't have an account yet.

        Getting fed up of having to scroll through the same posts each visit? When you register for an account, you'll always come back to exactly where you were before, and choose to be notified of new replies (either via email, or push notification). You'll also be able to save bookmarks and upvote posts to show your appreciation to other community members.

        With your input, this post could be even better 💗

        Register Login
        Reply
        • Reply as topic
        Log in to reply
        • Oldest to Newest
        • Newest to Oldest
        • Most Votes


        • Login

        • Don't have an account? Register

        • Login or register to search.
        Powered by NodeBB Contributors
        • First post
          Last post
        0
        • Categories
        • Recent
        • Tags
        • Popular
        • World
        • Users
        • Groups