DLMS/COSEM Limiter Object (Class 71) for Demand Limiting & Overload Tripping
-
Class 71 (Limiter) Configuration Guide
Class 71 provides autonomous on-meter monitoring to protect distribution transformers from local consumer overloads.
Architecture
- Monitored Value (Attribute 2): References Class 3/4 register, e.g. Active Power (+P)
1.0.1.7.0.255. - Threshold Normal (Attribute 3): e.g.
10000W (10 kW). - Threshold Emergency (Attribute 4): e.g.
15000W (15 kW during grid emergencies). - Min Over Threshold Duration (Attribute 5): e.g.
30seconds (avoids tripping on motor inrush current). - Action Over Threshold (Attribute 7): Calls script to open contactor (
Class 70). - Action Under Threshold (Attribute
: Calls script to reconnect or signal availability.
Configuring the debounce duration properly is critical to prevent nuisance tripping during air-conditioner startup spikes.
- Monitored Value (Attribute 2): References Class 3/4 register, e.g. Active Power (+P)
-
We set
min_over_threshold_durationto 45 seconds in our residential prepaid deployments. It successfully allows heat pump startup surges while cutting off sustained illicit overloads.
Hello! It looks like you're interested in this conversation, but you don't have an account yet.
Getting fed up of having to scroll through the same posts each visit? When you register for an account, you'll always come back to exactly where you were before, and choose to be notified of new replies (either via email, or push notification). You'll also be able to save bookmarks and upvote posts to show your appreciation to other community members.